660MW机组协调控制回路优化
程 艳 , 吴志国
大唐信阳发电有限责任公司,河南 信阳 464000
660MW unit coordinated control loop optimization
Chengyan ,wuzhiguo
Datang Xinyang power generation limited liability company, Henan Xinyang 464000
Abstract:660MW units of a certain power plant in the process of lifting load ,Existence main steam temperature fluctuations big even drastically reduce the nearly 40 degrees ,And the main steam pressure loop adjustment poorer quality unit, a serious threat to the safe and economic operation 。To solve this problem, put forward a series of suitable for their power of coordinated control loop optimization plans and implement this in minor repairs a scheme,After rev machine commissioning, solved after the above problems 。This paper is the the plant coordinated control loop optimization related problems were summarized in this paper.
Key words:Fluctuation deviation control optimization
摘要:某电厂660MW机组在升降负荷的过程中,存在主汽温波动大甚至快速降低近40度的情况,且主汽压力回路调节品质较差,严重威胁到机组安全经济运行。为切实解决这一系列问题,电厂提出了适合于自身的协调控制回路优化方案,并在小修中实施了这一方案,经过启机后调试,解决了上述问题。本文就此次该电厂协调控制回路优化的有关问题进行总结。
关键词: 波动;偏差;控制;优化
1前言
某电厂一台660MW机组自投产以来,在升降负荷的过程中多次出现汽温快速降低的情况,最低时降至560左右。主汽温过低,不仅影响到机组经济性(对高压锅炉而言,汽温每降2℃,锅炉效率会减少0.1%~0.2%),而且也会造成汽机末级的蒸汽湿度过大而损坏叶片。因此,温度快降的现象严重影响到机组的安全和经济运行。
为了改善汽温快降及主汽压偏差大的情况,保证机组的安全经济运行,该电厂特制定了自动优化及试验方案,并于2010年4月实施。
优化完成后,经过大量的试验数据及运行工况证实这一改造的意义重大,解决了负荷升降过程中汽温快速变化的问题,汽温、汽压满足模拟量自动控制系统验收规程2006要求。
CP0831_FC.doc
(1.38 MB, 下载次数: 11)
|